donf
Member
- Location
- Tidewater Virginia
I am preparing to teach a Commercial Services class this week. The topic, while not new to me, is one I have not had to teach in several years.
The last time I had to look at this code citation, it stated that a "Multi-outlet" branch circuit (cord and plug) could not be loaded to an amount greater than 80% of the OCPD. On a 20A circuit, the load could not be more than 16 Amps.
When I researched that using the 2017 code, I discovered that it reads, "...a receptacle shall not supply more than …." The 20 Amp receptacle lists 16 Amp in the table.
Here's my concern with my interpretation. As I read that citation, (in a commercial) environment, I could have several receptacles in a 20 amp circuit supplying loads of 12 Amps each, just for arguments sake, and still have a code compliant branch circuit.
I grant you that there is no way we can ever guarantee what load gets plugged into the receptacle, but am I reading and understanding this citation correctly?
The last time I had to look at this code citation, it stated that a "Multi-outlet" branch circuit (cord and plug) could not be loaded to an amount greater than 80% of the OCPD. On a 20A circuit, the load could not be more than 16 Amps.
When I researched that using the 2017 code, I discovered that it reads, "...a receptacle shall not supply more than …." The 20 Amp receptacle lists 16 Amp in the table.
Here's my concern with my interpretation. As I read that citation, (in a commercial) environment, I could have several receptacles in a 20 amp circuit supplying loads of 12 Amps each, just for arguments sake, and still have a code compliant branch circuit.
I grant you that there is no way we can ever guarantee what load gets plugged into the receptacle, but am I reading and understanding this citation correctly?