NECuser
Member
- Location
- New Jersey
2011 NEC Section 210.4(B) states: "Disconnecting means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates." I received correspondence from another engineer indicating he interprets this to mean "All wires, which includes all hot and neutral wires, of a single wiring installation must be disconnected with one device (circuit breaker)...Simply stated, one neutral wire shall not service two circuits...Therefor, a 3 wire 120/240 or a 240/480 system shall not use 2 circuit breakers, one for each hot line because there is only one neutral". His recommendation proposed two alternatives; either use a separate neutral for each circuit or use a 2-pole circuit breaker. I disagree with his interpretation. My understanding is the neutral wire is not impacted by NEC 210.4(B) because the neutral wire is considered a grounded conductor. My proposed response is going to require installation of 2 single pole circuit breakers with identified handle tie [not a two-pole circuit breaker (in order to limit the number of lights that would turn off if maintenance needed to work on the circuit)]. Please confirm if my understanding that the neutral is not impacted by 210.4(B) is correct and my proposed response is feasible.