In Article 210.8(B)5), it is required to have GFCI protection
of receptacles installed within 6 ft. of the outside edge of a sink / lav.
Exception #2 to Article 210.8(B)(5) says that" "For receptacles located
in patient care areas of health care facilities other than those covered
under 210.8(B)(1), GFCI protection shall not be required."
In this Article, the Exception overrides the general rule.....Is there a
an Article or section in the NEC similar to the one in the IBC where,
" ...where there are conflicts between standards, the more
restrictive shall apply?"
Does Article 210.8(B)(5) override Exception # 2 because it is
more restrictive, ...or was this Exception allowed specifically for
sinks / lavs. in Patient Care areas and their close proximity to required
receptacles ?
* * * *