Article 210- Fixture required

Status
Not open for further replies.
Article 210.70 (A) Dwelling Units states that "In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (A)(2) and (A)(3). Simple question- Does a light fixture have to be installed if the a lighting outlet is provided in the ceiling to pass inspection?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Article 210.70 (A) Dwelling Units states that "In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (A)(2) and (A)(3). Simple question- Does a light fixture have to be installed if the a lighting outlet is provided in the ceiling to pass inspection?
Around here they may require it but it is a question that many disagree on. I would call the inspector and see what they require.
 

dicklaxt

Senior Member
Thats one of those(Art) that I say only an outlet is req'd and does not include the fixture,,,,,,,,How can this one be misinterpreted:?

dick
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Thats one of those(Art) that I say only an outlet is req'd and does not include the fixture,,,,,,,,How can this one be misinterpreted:?

dick
I agree but as everything in the NEC there are areas that will insist that the light be installed. Now the building code may require the light to be installed-- not sure of that. Also how can they require a lamp to be there if the lighting outlet is a switched recep.? They can't so it would stand to reason that the light is not required to be installed.

I know that years ago the inspections dept in some areas would only allow a few temp. lights like keyless etc. They wanted to make sure the fixtures were Listed. Not sure they do that anymore.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This is one that has been answered in an ROP.

1-38 Log #573 NEC-P01
Final Action: Reject
(100.Lighting Outlet)

__________________________________________________ ___________​
Submitter:​
Alan H. Nadon, City of Elkhart, IN

Recommendation:
Revise as follows:
Lighting Outlet. An outlet having intended for the direct connection of a
lampholder, a luminaire (lighting fixture), or a pendant cord terminating in a
lampholder, that is directly connected .

Substantiation:
Intent cannot be determined during an inspection. A junction
box with a blank cover, even one containing switched conductors, does not
provide the illumination needed for persons to move about safely thus
preventing accidents.

Panel Meeting Action: Reject
70-22​
Report on Proposals A2007​
? Copyright, NFPA NFPA 70

Panel Statement:
The proposed definition would require a luminaire
wherever a lighting outlet is installed. Code rules dictate where lighting is
required. CMP-1 refers the submitter to the panel action and statement on
Proposal 1-39.

Number Eligible to Vote: 12
Ballot Results:
Affirmative: 12
__________________________________________________ _______