Hey all,
I had some questions regarding the changes to Article 215.2(A):
I'm getting some City Officials commenting that my feeders are undersized to some panels. Is this code section telling me that I would need to size my feeder for the connected load plus 125% of any continuous loads, rather than sizing my feeder for the diversified load of the panel (50% of receptacles after the first 10KVA, etc)?
What is the intent for these changes in the 2014 code? The more I read it, the more it makes me feel like any diversity or demand factors are rendered useless. Surely, this is not the intent.
I had some questions regarding the changes to Article 215.2(A):
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(1) General. Feeder conductors shall have an ampacity not
less than required to supply the load as calculated in Parts
III, IV, and V of Article 220. Conductors shall be sized to
carry not less than the larger of 215.2(A)(1)(a) or (b).
(a) Where a feeder supplies continuous loads or any
combination of continuous and noncontinuous loads, the
minimum feeder conductor size shall have an allowable
ampacity not less than the noncontinuous load plus
125 percent of the continuous load.
(b) The minimum feeder conductor size shall have an
allowable ampacity not less than the maximum load to be
served after the application of any adjustment or correction
factors.
I'm getting some City Officials commenting that my feeders are undersized to some panels. Is this code section telling me that I would need to size my feeder for the connected load plus 125% of any continuous loads, rather than sizing my feeder for the diversified load of the panel (50% of receptacles after the first 10KVA, etc)?
What is the intent for these changes in the 2014 code? The more I read it, the more it makes me feel like any diversity or demand factors are rendered useless. Surely, this is not the intent.