ControlsRPS
Member
- Location
- earth
- Occupation
- Automation Electrical Designer & Programmer
I am a member on other forums and before I chastise someone for this suggestion I want to see what other electricians think.
The way I read Article 220, you can only use nameplate data, or standards to calculate load when sizing electrical service conductors. Does anyone know if using an Ammeter to check load is accepted as an acceptable method for service entry calculation?
The problem: Existing single family home, All appliances are electric, forum member wants to add a 80A EV-Charger.
- 3 quotes from local electricians all say service needs to be upgraded because service entry 200A doesn't have capacity to add 19.2KvA into the existing.
Lots of other members chiming in: Throw an Ammeter on there and see what you are actually using before you upsize your service.
The way I read Article 220, you can only use nameplate data, or standards to calculate load when sizing electrical service conductors. Does anyone know if using an Ammeter to check load is accepted as an acceptable method for service entry calculation?