wwhitney
- Berkeley, CA
- Retired
To improve my understanding, and explore the options in Article 220 beyond the standard calculations in Part III, I came up with the following example for a fairly modest but realistic all-electric dwelling unit: 1200 sq ft, no extra SABCs/laundry, and equipment nameplate data as follows:
Range: 12 kW
Dryer: 24A @ 240V = 5760 VA
Heat Pump: 240V, Compressor RLA 12A, Fans 1A, MCA 16A
Dishwasher: 1200W
Water Heater: 4500W
ERV: 2.5A @ 120V = 300VA
Bath fan: 0.27A @ 120V = 32VA
Range Hood: 2.4A @ 120V = 288 VA
Disposal: 6A @ 120V = 720VA
(The ERV and disposal are marked with HP ratings as well, but 430.6(A)(1) Exception 3 tells us to use the FLA when a listed motor driven appliance is marked with both FLA and HP on the nameplate).
To start with the standard calculation in Part II, some preliminaries:
- The general lighting and receptacle load is 3VA * 1200 sqft + 3 specified circuits (SABC and Laundry) * 1500 VA/circuit = 8100VA. This is subject to first 3 kVA @ 100%, rest @ 35%.
- Range load is 8 kVA for one dwelling unit. Table 220.55 tells us to add 3 kVA each for a second or third range.
- Dryer nameplate exceeds 5000VA, so we use the nameplate.
- Heat pump load @ 100% is 13A * 240V = 3120 VA, with 25% of the largest motor as 25%*12*240V = 720 VA.
- The last 6 items count as appliances and total 7040 VA. They can get a 75% factor per 220.53.
In the calculation for 1 dwelling unit, I'm going to separate out the "base" part (which doesn't increase with more units) from the "scalable part" (which does increase). The upshot for 1-3 dwelling units:
- On the general lighting and receptacle load, there's 65% * 3000VA = 1950VA base and 35% * 8100 VA = 2835 VA scalable.
- For the range, it's 5 kVA base and 3 kVA scalable
- Dryer is 5760 VA scalable (no reduction allowed for 1-4 dryers in Table 220.54)
- The heat pump load is 720VA base (25% of largest motor), 3120VA scalable.
- The appliances are 75% * 7040 VA = 5280 VA scalable.
Adding these up, 1 dwelling unit is 7670 VA base plus 19,995 VA scalable. That totals 27,665 VA, or 115A.
Then for 2 dwelling units, it's 7670 VA + 2 * 19,995 VA = 47,660 VA, or 199A. And for 3 dwelling units it's 7670 VA + 3 * 19,995VA = 67,655 VA, or 282A.
Any errors above? If that's all correct, I'll continue with the Part IV options in the next post.
Cheers, Wayne
Range: 12 kW
Dishwasher: 1200W
Water Heater: 4500W
Cheers, Wayne