i have 6 seperate buildings that i want to install outside lighting on and to feed from 1 house meter in 1 building.can i do this or do i have to put in seperate house meters in each building to pick up house lighting.
 

Nick

Senior Member
Re: article 225.30

You can do this but the circuit(s?) that go to each building have to have a service rated disconnect where it (they) enters the structure and the equipment grounding conductor must tie to the buildings grounding electrode system.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: article 225.30

rick,
Do each of the six buildings have their own service? If so check with the AHJ. It appears that the intent of 225.30 and 230.2 is to limit each building to a single source of supply. The words do not exactly say that, but I would clear it with the AHJ before proceeding.
Don
 

rickk

Member
Re: article 225.30

THANKS NICK, I CHECKED WITH THE BUILDING INSPECTER AND THEY OK'D PUTTING A DISCONNECT AT EACH BUILDING WITH A SIGN.
 