Article 225.32 Location. The disconnecting means shall installed be either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. ect.,ect.,
Residential House with main 200A service on detached garage the underground to house
Our 200A disconnect is in basement inside house panel on wall 5' from where conductors pass through basement wall
is this a readily accessible location nearest the point of entrance of the conductors?
Electrical Inspsector says disconnect has to be outside and of course he is saying this at final inspection after concrete and landscaping is covering underground conductors
I contend we are meeting the requirements of Article 225.32 What say you?