Article 225.39 has been discussed here quite a bit and I don't agree with the interpretation by many. The section talks about the feeder disconnect. I hear everyone say- even myself- that this only affects the disconnect and I believe they are talking about the disconnect at the garage.
Example- if we feed a detached garage at a dwelling then IMO, the feeder disconnect is the overcurrent protective device at the main building. If 225.39(D) requires a 60 amp disconnect for the feeder then wouldn't you be required to run a 60 conductor to the garage? IMO, you must run a 60 amp feeder but I never see it enforced.
Example- if we feed a detached garage at a dwelling then IMO, the feeder disconnect is the overcurrent protective device at the main building. If 225.39(D) requires a 60 amp disconnect for the feeder then wouldn't you be required to run a 60 conductor to the garage? IMO, you must run a 60 amp feeder but I never see it enforced.
225.39 Rating of Disconnect. The feeder or branch-circuit disconnecting means shall have a rating of not less than the calculated load to be supplied, determined in accordance with Parts I and II of Article 220 for branch circuits, Part III or IV of Article 220 for feeders, or Part V of Article 220 for farm loads. Where the branch circuit or feeder disconnecting means consists of more than one switch or circuit breaker, as permitted by 225.33, combining the ratings of all the switches or circuit breakers for determining the rating
of the disconnecting means shall be permitted. In no case shall the rating be lower than specified in 225.39(A), (B), (C), or (D).