This one is beating me to death. Weare currently turning an old 200 room hotel in to a 50 unit condo. The calcualted load is a little over 2900 amps.
There wasnt room to install 5 meterpacks with disconnects grouped in one location.
We installed 3 on the back and two on the front. The POCO has installed their service to these meter packs and are thrilled at the installation.
Local inspector claims all disconnects have to be in one location and says this current installation is a direct violation of the NEC.
I can think of several arguments but please help me prove him wrong or convince me I am wrong.
It is a money pit to try and satisfy his theory.
I need article #s comments
Thanks guys.