Re: Article 230 - Services
I do not understand your routing, as you have two contradictory statements:
Originally posted by samblv: Building A has the switchboard you want to feed Building C with. Which in turn, will feed building B.
This description conflicts with the following:
Can the feeder be routed thru Buildings A and B?
The conflict is that the first statement says power goes from A to C and then to B, whereas the second statement says that power goes from A to B to C.
This is what I think you are trying to describe. Please tell me if I have it right or wrong:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Power comes from the utility (we don't know where the meter is) to a switchboard in Building A.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">There is a breaker on that switchboard, and it provides power to some type of panel in Building C.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">There is a breaker on that panel (in Building C), and it provides power to some type of panel in Building B.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">If that is the correct description, then the wires coming into Building A are "service conductors," and the wires going to Buildings C and B are "feeders."