ju
Member
- Location
- New Jersey
I have a 1200 amp service with a 1200 amp main. A EC who needs a 200 amp service for a relay station which is on the roof about 200 feet away. He would like to tap off the 1200 amp bus on the load side of the main with 3/0 copper conductors and feed the new meter and then go to a 200 amp serviceable disconnect with 200 amp fuses. The conductors are located a little under 25 feet from the 1200 amp main to the meter. It is my opinion that this is in violation of Article 240.21(2)which requires the size of the conductors to be one third the rating of the overcurrent device. In my opinion, the conductors should be rated for 400 amps with a main of 400 amps and then continue on to the meter with 600 kcmil to the second disconnect. The second disconnect would then be fused for 200 amps using 3/0 copper wire to the panel on the roof. Can anyone help me ???? I would appreciate your input.