Say I have a 240V 3P3W corner grounded system, and I use panelboards with just 2 busbars for the ungrounded conductors along with a terminal bar for the grounded conductors. OCPD is appropriately rated 240V to ground.
Now I install a 2 pole 40A breaker with (2) #8 Cu ungrounded conductors, a #10 Cu grounded conductor, and a #10 EGC to supply a small panelboard that supplies a 30A 3-phase load plus a 10A 2-wire load supplied between the two ungrounded conductors.
Does this comply with the NEC? If not, what code section is violated? [Note that an ungrounded conductor could fault to the #10 grounded conductor and carry 40A without tripping the OCPD, but the same is true of the #10 EGC.]
Cheers, Wayne
Now I install a 2 pole 40A breaker with (2) #8 Cu ungrounded conductors, a #10 Cu grounded conductor, and a #10 EGC to supply a small panelboard that supplies a 30A 3-phase load plus a 10A 2-wire load supplied between the two ungrounded conductors.
Does this comply with the NEC? If not, what code section is violated? [Note that an ungrounded conductor could fault to the #10 grounded conductor and carry 40A without tripping the OCPD, but the same is true of the #10 EGC.]