I am writing to ask about the overcurrent protection that is described in Section 240-I. First, I have read through the sections relating to overcurrent protection for cables rated 600V or less. I have noticed that the wording seems much more specific regarding what is allowed for protecting cables in the 600V or less category. In contrast, the wording for overcurrent protection of cables in the over 600V category seems much less stringent.
Article 240-100 (b) simply states that the overcurrent protective devices shall be capable of detecting and interrupting all values of current in excess of their trip settings. This article does not seem to provide any limitations on what can be set.
Article 240-100 (c) states that the overcurrent protetive devices must protect agianst excessive temperatures caused by short-circuit currents.
Article 240-101 (a) allows fuses to be sized up to three times the ampacity rating of the cable. The long time trip element setting of a breaker is allowed to be set up to six times the ampacity rating of the cable.
Allow me to use an example from Table 310-79. The cable is 2/0 copper, Type MV-90, with an ampacity rating of 200 amperes. Based on my understanding of Article 240-101 (a) this cable could be protected against overloads with a long time trip element setting of the circuit breaker at 1200 amperes. Is this the intent of Article 240-101 (a)? Article 240-100 (c) requires protection against damaging temperatures caused by short circuit currents, but Article 240-101 (a) seems to allow damaging tmeperatures to the cable caused by continuous load current.
Can anyone please provide some clarifications on these Articles of the NEC?
Article 240-100 (b) simply states that the overcurrent protective devices shall be capable of detecting and interrupting all values of current in excess of their trip settings. This article does not seem to provide any limitations on what can be set.
Article 240-100 (c) states that the overcurrent protetive devices must protect agianst excessive temperatures caused by short-circuit currents.
Article 240-101 (a) allows fuses to be sized up to three times the ampacity rating of the cable. The long time trip element setting of a breaker is allowed to be set up to six times the ampacity rating of the cable.
Allow me to use an example from Table 310-79. The cable is 2/0 copper, Type MV-90, with an ampacity rating of 200 amperes. Based on my understanding of Article 240-101 (a) this cable could be protected against overloads with a long time trip element setting of the circuit breaker at 1200 amperes. Is this the intent of Article 240-101 (a)? Article 240-100 (c) requires protection against damaging temperatures caused by short circuit currents, but Article 240-101 (a) seems to allow damaging tmeperatures to the cable caused by continuous load current.
Can anyone please provide some clarifications on these Articles of the NEC?