Hi Mike,
I wonder if you can answer this question and settle an argument?? In a downtown high-rise building in which we are doing a tenant fit-out, there are three 100A MLO panelboards each fed with 4#2 AWG from a single 100A fused disconnect switch thru a junction box. Inside the junction box, the three panel feeders are spliced to the incoming feeder from the 100A fused disconnect switch.
Could any of these panel feeders be considered a tap under any of the rules of Article 240 of the NEC or is this simply a tee splice? Are there any code restrictions on this application?
A tap is usually considered to be a smaller conductor than the feeder conductor. In this case there is no reduction of the feeder size, therefore it does not constitute a tap.
Your thoughts would be appreciated..
I wonder if you can answer this question and settle an argument?? In a downtown high-rise building in which we are doing a tenant fit-out, there are three 100A MLO panelboards each fed with 4#2 AWG from a single 100A fused disconnect switch thru a junction box. Inside the junction box, the three panel feeders are spliced to the incoming feeder from the 100A fused disconnect switch.