We have a job underway and I'm looking for a bit more clarification to verify that I truly see where the electrical engineer is coming from. The project is a school with two services, both fed from separate utility transformers (both primaries are primary metered). The high school service is existing and we are not scheduled to do any work, at the moment, on it. The middle school service is newly revamped.
When I asked for clarification on a note from the engineer on a note that requires a 3/0 conductor from the new middle school service to be routed and bonded to the existing high school service, their response included NEC 2011 Article 250.58 and a link to an article by EC&M. Now, looking at the information that they have provided, it seems that the article covers two separate services supplied by the same transformer. This is the part I'm unclear on. I understand that they may be attempting to mitigate potential differences between the two systems, but there is clear separation between the two services as they serve two buildings separated by a firewall. I may be missing the mark completely.
Another though I had just had is that this situation might be similar to a row of "main street" buildings that have been built to share a wall, but not necessarily a service served by the same transformer. Even if they were served by the same transformer, would I still be required to bond the services through the building? Certainly not especially if they were served by different transformers. Maybe I'm reading into it too much, but I've always tried to adhere to the rule of if it doesn't need to be energized, don't bond it.
I apologize for the lengthy post and appreciate your time and assistance on this.
I also apologize if this discussion had been covered in a previous post, there is a lot of great content available on this forum.
We have a job underway and I'm looking for a bit more clarification to verify that I truly see where the electrical engineer is coming from. The project is a school with two services, both fed from separate utility transformers (both primaries are primary metered). The high school service is existing and we are not scheduled to do any work, at the moment, on it. The middle school service is newly revamped.
When I asked for clarification on a note from the engineer on a note that requires a 3/0 conductor from the new middle school service to be routed and bonded to the existing high school service, their response included NEC 2011 Article 250.58 and a link to an article by EC&M. Now, looking at the information that they have provided, it seems that the article covers two separate services supplied by the same transformer. This is the part I'm unclear on. I understand that they may be attempting to mitigate potential differences between the two systems, but there is clear separation between the two services as they serve two buildings separated by a firewall. I may be missing the mark completely.
Another though I had just had is that this situation might be similar to a row of "main street" buildings that have been built to share a wall, but not necessarily a service served by the same transformer. Even if they were served by the same transformer, would I still be required to bond the services through the building? Certainly not especially if they were served by different transformers. Maybe I'm reading into it too much, but I've always tried to adhere to the rule of if it doesn't need to be energized, don't bond it.
I apologize for the lengthy post and appreciate your time and assistance on this.
I also apologize if this discussion had been covered in a previous post, there is a lot of great content available on this forum.