Article 250.66 Note #2 States: Where there are no service-entrance conductors, the grounding electrode conductor size shall be determined by the equivalant size of the largest service entrance conductor required for the load to be served.
I have a 400 amp main switch with a 350 kcmil ungrounded service entrance conductors present which i sized the GEC at #2 cu using Table 250.66. However the inspector stated that on a service lateral application i have to size the GEC to 250.66 Note #2 then using Table 310-16 to find wire size of the load to be served (400 amp) then going back to table 250.66 with your higher wire size. Any input on this? Is this true with a service lateral application with srvice entrance conductors present?
I have a 400 amp main switch with a 350 kcmil ungrounded service entrance conductors present which i sized the GEC at #2 cu using Table 250.66. However the inspector stated that on a service lateral application i have to size the GEC to 250.66 Note #2 then using Table 310-16 to find wire size of the load to be served (400 amp) then going back to table 250.66 with your higher wire size. Any input on this? Is this true with a service lateral application with srvice entrance conductors present?