I need an expert opinion on the meaning of 250.92 B-3 which says that "threadless couplings and connectors where made up tight for metal raceways" are an acceptable method of bonding at service equipment". The paragraph after method B-4 says that bonding jumpers are required around eccentric and concentric KO's, then the last sentence says "Standard locknuts or bushings shall not be the sole means for the bonding required by this section". It is my understanding from this, and that of my engineering consultant, that this means a steel EMT connector made up tight to an enclosure is an acceptable method of bonding service equipment together and bonding the grounding electrode conductor raceway to the enclosure.
I am currently on a job where the inspector disagrees. They interpret the sentence that standard locknuts or bushings are not allowed as the sole means of bonding to apply to section B-3 also. Contrary to what B-3 says, they claim I need grounding bushings on EMT connectors connecting a 1600A 480-V Utility Section and the Main disconnect section as well as on the EMT connector connecting the ground electrode conduit. I have tried to point out to them that if this were true, then 250.92 B-3 is erronious and the requirement to bond around concentric KO's is superflous as it means you have to bond around everything anyway. The pictures in the NEC Handbook on this section seems to confuse rather then help them. They indicated if I could produce an expert opinion supporting my understanding they would consider it. HELP!!!
dsullada
Nor Cal Electric Co.
Contracting 48 years
I am currently on a job where the inspector disagrees. They interpret the sentence that standard locknuts or bushings are not allowed as the sole means of bonding to apply to section B-3 also. Contrary to what B-3 says, they claim I need grounding bushings on EMT connectors connecting a 1600A 480-V Utility Section and the Main disconnect section as well as on the EMT connector connecting the ground electrode conduit. I have tried to point out to them that if this were true, then 250.92 B-3 is erronious and the requirement to bond around concentric KO's is superflous as it means you have to bond around everything anyway. The pictures in the NEC Handbook on this section seems to confuse rather then help them. They indicated if I could produce an expert opinion supporting my understanding they would consider it. HELP!!!
dsullada
Nor Cal Electric Co.
Contracting 48 years