stevewilcox
Member
- Location
- San Diego, California
I too have some questions involving this topic. We have a 3/0 bare copper GEC in a 1" GRC connected to J-box and Substation with a Myers Hub @ J-box and Locknuts @ Substation. Both Holes were punched. Our inspector is saying that we need to include a 3/0 bond (same size as GEC) at the both ends of the conduit because of "Choke Effect". At first this seemed rediculous --bare copper in rigid??? Seemed bonded to me. But I can see that this is a legit concern. However, I'm also seeing in the code (my take) that it's not required because 250.92 (B)(2) electrcal continuity is insured by connection utilizing threaded bosses on enclosures where made up wrenchtight & 250.64 (E) ferrous metal enclosures for GEC shall be electrically continuous...
Thoughts? To appease the inspector we installed a Burndy fitting @ the substation that clamps the conductor as it exits the conduit, but not at the other end where the Meyers Hubs are employed. In this situation should we have to bond both ends? From reading the other threads it seems up in the air a little.
Thoughts? To appease the inspector we installed a Burndy fitting @ the substation that clamps the conductor as it exits the conduit, but not at the other end where the Meyers Hubs are employed. In this situation should we have to bond both ends? From reading the other threads it seems up in the air a little.