I've got a guy that states a residential alarm or security system (I'm guessing any alarm for that matter) is not required to be grounded.
I'm citing 250.20 A(2) as the transformer in a typical system is ungrounded at the outlet they typically plug into, albeit the HV feed is grounded.
He's stating that 250.112 (I) says no grounding needed, however the code references required in Part II and Part VIII.
I also stated that 250.162 A (1) and (2) are what modifies the requirement regarding the field wiring needing a ground, which is what changes a C1 to a
C2/C3 circuit.
His argument is saying why have a C2 or C3 circuit if there's restrictions?
I was taught and my understanding is that a system/panel was always required to be grounded, however a manufacturer's instructions supercede the
code, if they specifically tell you to not ground the system/panel, since you're installing I/A/W the manufacturer's instructions.
I'm citing 250.20 A(2) as the transformer in a typical system is ungrounded at the outlet they typically plug into, albeit the HV feed is grounded.
He's stating that 250.112 (I) says no grounding needed, however the code references required in Part II and Part VIII.
I also stated that 250.162 A (1) and (2) are what modifies the requirement regarding the field wiring needing a ground, which is what changes a C1 to a
C2/C3 circuit.
His argument is saying why have a C2 or C3 circuit if there's restrictions?
I was taught and my understanding is that a system/panel was always required to be grounded, however a manufacturer's instructions supercede the
code, if they specifically tell you to not ground the system/panel, since you're installing I/A/W the manufacturer's instructions.