You mean not land the GEC within the first five feet of where the pipe enters the building?
2014 NEC
250.68
(C) Grounding Electrode Connections. Grounding elec- trode conductors and bonding jumpers shall be permitted to be connected at the following locations and used to extend the connection to an electrode(s):
(1) Interior metal water piping located not more than 1.52 m (5 ft) from the point of entrance to the building shall be permitted to be used as a conductor to interconnect elec- trodes that are part of the grounding electrode system.
Exception: In industrial, commercial, and institutional build- ings or structures, if conditions of maintenance and supervi- sion ensure that only qualified persons service the installation, interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall be permitted as a bonding conductor to interconnect electrodes that are part of the grounding electrode system, or as a grounding electrode conductor, if the entire length, other than short sections pass- ing perpendicularly through walls, floors, or ceilings, of the interior metal water pipe that is being used for the conductor is exposed.