Article 300.20: Grouping neutrals in a different conduit than hots

noahff

Member
Location
Washington, USA
Occupation
Electrical Engineer
We have an installation where the hot wires (3 phase, three of each phase) were installed in a separate conduit to the respective nine neutrals, and we are concerned this might be in violation of Article 300.20. Conduit is ferrous, and we don't have any shared neutrals. Is this a problem? I think all the fields would cancel out in each conduit. Any help would be much appreciated. :)
 
These are two wire circuits and the hot and neutral of each circuit must be installed within the same ferrous raceway.
 