F Frass New member Location Virginia May 12, 2016 #1 Does article 300.20 apply to medium voltage cable? 15kv shielded cable.
roger Moderator Staff member Location Fl Occupation Retired Electrician May 13, 2016 #2 Theory would say yes. Roger
M MattS87 Senior Member Location Yakima, WA May 13, 2016 #3 300.35 - Requirements for over 1000V directs you back to 300.20 so yes.