I have been working outside the industry for a couple of years and was encouraged by my director to help out (design) with the data/phone cabling of our new building. After all the meetings, design work, quotes for parts, etc, I was contacted by the GC that it was time to install my support system.

Support system? I informed him that in all the other buildings in the area that I had done in the past, I always supported my cabling with j-hooks suspended from the ceiling grid support wires. He said that according to the NEC article 300.11, I can't do that anymore.

I contacted my parts vendors to see if this was true and they were unable to supply me with a positive yes or no answer. I am unable to find anything on the internet that I can quote to the GC. Is this true?

Some articles say install your own support wire, but the GC told me they would have to be fastened to the grid, what's the difference?

I am always careful not to disturb the height of the ceiling, but this building has a 25 foot airspace above the drop-tile ceiling. It will be costly for me to run allthread or gridwire of that length.

I saw in an article on the Mike Holt website the following phrase, "Article 300 contains the general requirements for all wiring methods included in the NEC. However, this article doesn't apply to signaling and communications systems, which are covered in Chapters 7 and 8, except as specifically referenced in those chapters."

Does this help? Can someone give me a black and white answer? Please help.
Thanks!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Looking at 800.24

800.24 Mechanical Execution of Work
Communications circuits and equipment shall be installed in a neat and workmanlike manner. Cables installed exposed on the surface of ceilings and sidewalls shall be supported by the building structure in such a manner that the cable will not be damaged by normal building use. Such cables shall be secured by straps, staples, hangers, or similar fittings designed and installed so as not to damage the cable. The installation shall also conform with 300.4(D) and 300.11.

Now we go to 300.11

300.11 Securing and Supporting
(A) Secured in Place Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened in place. Support wires that do not provide secure support shall not be permitted as the sole support. Support wires and associated fittings that provide secure support and that are installed in addition to the ceiling grid support wires shall be permitted as the sole support. Where independent support wires are used, they shall be secured at both ends. Cables and raceways shall not be supported by ceiling grids.

(1) Fire-Rated Assemblies Wiring located within the cavity of a fire-rated floor?ceiling or roof?ceiling assembly shall not be secured to, or supported by, the ceiling assembly, including the ceiling support wires. An independent means of secure support shall be provided and shall be permitted to be attached to the assembly. Where independent support wires are used, they shall be distinguishable by color, tagging, or other effective means from those that are part of the fire-rated design.