- Milwaukee, WI
We have an issue where our incoming service conductors (24.9kV) enter the building at an expansion joint with movemetn +-2" in both the x and y directions. We would like the conduits leaving the exterior junction boxes to not be rigidly attached to the box but bond the conduits to the box for continuity. Below is a sketch of what we would like to do, does anyone see this as an acceptable variance to the requirements of 300.10?