gblakowski
New member
- Location
- New York
I ran a feed to a 120/208 volt 75 hp fire pump motor with the wire size based on a running load current of 188 Amps X 125%. I used 250 KCML copper rated in the 75 degree column of 310.16 for 255 Amps. The electrical inspector tells me my wire is undersized due to the fact that I should have based my running amps from the hp table of Article 430. I checked the code, and he is correct. Even though I am using 90 degree C wire, I must use the 75 degree C column due to the terminal ratings of 75 degrees. Could I use a 90 degree C rated barrel / reducing splice to increase my wire size to 350 KCML in the panel and controler in order to be able to use the 90 degree column of 310.16 therefor making my 250 KCML wire legal?