This article refers to conductors operated above 2000 volts. Is this 2000 volts with respect to ground?
charlie b said:Yes. "Ground" is where the electrons would go, if the insulation were to breakdown. So insulation systems are rated in terms of voltage to ground.
You are certainly free to disagree. But you have not presented a strong argument in favor of the notion that "phase to phase" is intended, by default, unless "voltage to ground" is explicitly stated. The voltage rating of any component is based on the ability of its insulation system to prevent leakage from "where the current is" to "where the current should not be." For a cable, the place that "the current is" is the metal conductor, and the place that "the current should not be" is beyond the outer layer (be it insulation, shielding, jacketing, or armor). So what is there just beyond that outer layer? Another conductor? No, it is planet Earth, and things that are electrically connected to planet Earth.steve66 said:Charlie: I have to disagree that this is not voltage to ground, this could be phase to phase voltage. Other articles (like 215.10 - GFP protection for feeders) specifically say "voltage to ground". 310.6 only says voltage.
Never in our industry does anybody express or speak about AC waveforms in terms of their peak values. What never? No never! What NEVER? Well, HARDLY EVER! (With apologies to Sir William Schwenk and Sir Arthur.)steve66 said:In addition, I don't think they mean RMS voltage. My take would be anything over 2000V peak.