pnp71
New member
- Location
- Lewisport, Ky
310.10(H)(4) States that if I use parallel conductors, (No mention of raceway design), I'm required to comply with 310.15(B)(3)(a). I will agree that if the parallel conductors are in the same raceway I should derate per the table. Since I am installing the parallel feeders in seperate raceways with no more than three current carrying conductors in a raceway I don't believe this derate should apply. What am I missing?