I'm designing a vertical riser to run approximately 15 floors. This will consist of 3 inch EMT with pull boxes on each floor. So there will be a 3 inch on the bottom, a 3 inch comming out the top and in addition on each floor there will be 3/4 inch LB comming off top or bottom to take a single circuit over to the IDF room. Conductors in the 3 inch pipe will be no larger than #6. So 2 questions:
1. 314.28(A)(1) only applies if you are using 4 AWG or larger. What then applies when you've got smaller conductors.
2. I assume the above referenced section will give me an appropriately sized box (if perhaps over kill) as far as the length (or in this case height) is concerned, but what about the dimensions of the sides with the conduit comming into it. I assume an 8 by 8 would be ample, but what is the rule. I need to make these boxes as small as possible because of a shortage of space.
Thanks,
Mike
1. 314.28(A)(1) only applies if you are using 4 AWG or larger. What then applies when you've got smaller conductors.
2. I assume the above referenced section will give me an appropriately sized box (if perhaps over kill) as far as the length (or in this case height) is concerned, but what about the dimensions of the sides with the conduit comming into it. I assume an 8 by 8 would be ample, but what is the rule. I need to make these boxes as small as possible because of a shortage of space.
Thanks,