Anyone ever invoked 358.30 (B) ['05]?
I have an application where strapping isn't possible... I'll post pics if you don't believe me! (It's fished between the roof and the truss, with truss on 6' centers, so the "framing members" are closer than the 3 m [10'] minimum.)
Don't know if inspector will let me by with this rule.
Any experience with this type of install, anyone at all?
The NEC said:358.30 Securing and Supporting. EMT Shall be installed as a complete system in accordance with 300.18 and shall be securely fastened in place and supported in accordance with 358.30 (A) and (B).
...
(B) Supports. Horizontal runs of EMT supported by openings through framing members at intervals not greater than 3 m (10 ft) and securely fastened within 900 mm (3 ft) of termination points shall be permitted.
I have an application where strapping isn't possible... I'll post pics if you don't believe me! (It's fished between the roof and the truss, with truss on 6' centers, so the "framing members" are closer than the 3 m [10'] minimum.)
Don't know if inspector will let me by with this rule.
Any experience with this type of install, anyone at all?