article 404.8b Voltage between adjacent devices

Status
Not open for further replies.

jdou

Member
Location
katy, texas
I am currently redoing the hibay lighting in my companys' shop. They have had outside contractors in to build new offices, walls, remodeling etc. When I was recruited to do this-ha- I did a little research as to how the shop lighting was laid out, and found the existing 277v hibay lighting on 2 circuits, a phase and b phase, and on 2 switches within the same switchbox. As it stands, it seems that there is 480v between the 2 devices in this switchbox, which is a code violation per 404.8b. The "powers at be" that I must deal with argue that the devices are considered "individually" and do not exceed 300v.
If the switches were on the same phase,but still separate circuits, would this still be a violation as the voltage between the 2 devices would be 0?
Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
As it stands it is a violation.

If you make each of the circuits on the same phase it will meet code.

You can also get a barrier for many boxes that will meet code.
 

480sparky

Senior Member
Location
Iowegia
Then you have 480 volts between adjacent devices. The NEC pretty much makes it clear what to do.

If they're on the same phase, then you would have 0 volts between them, and no barriers are needed. But my guess is they need to be on separate phases because it's a MWBC.
 