wwhitney
- Berkeley, CA
- Retired
2023 NEC 424.22(B) says "Resistance-type heating elements in electric space-heating equipment shall be protected at not more than 60 amperes. Equipment rated more than 48 amperes and employing such elements shall have the heating elements subdivided, and each subdivided load shall not exceed 48 amperes."
Now various sections refer to "the supplementary over-current protective devices for the subdivided loads," like 424.22(C). But I don't actually see a statement in Article 424 of the form "Subdivided loads shall be provided with supplementary over-current protection devices." Did I miss it? Or is it acceptable to install a piece of fixed electric space heating equipment that uses say 2x 32A resistance-type heating elements, and supply it with 2x 40A branch circuits, with no supplementary OCPD?
[I have not looked at the applicable UL standard; if it requires supplementary OCPD for subdivided loads, the question would be moot, as such equipment would not exist. That would also explain why Article 424 seems to assume such supplementary OCPD for subdivided loads; still seems odd that the NEC would omit the explicit requirement.]
Thanks, Wayne
Thanks, Wayne