Re: Article 427 & Heat Trace
We have been installing a lot of 277 volt heat trace in the past 3 or 4 years.
The GFP protection is a pain, essentially a shunt trip breaker with an external "donut" CT that mounts in the gutter space of the panel.
The breaker is of course 277 volt but the control circuit is 120 volt
so now you need to bring in a seperate 120 volt circuit and jump a hot and neutral in and out of each breaker, plus 4 control wires from each breaker to the CT, run the hot and neutral for that circuit through the CT, the hot ending up on the breaker, and the neutral to the neutral bar.
One problem with this is that the loss of the 120 volt circuit makes the breakers not GFP anymore.
I have never seen this addressed, I would like some sort of warning given on the loss of control power.
If you are at all interested in keeping it neat, it will take the better part of a day to do this.
Most times 20 amp circuits but 8, 6 or 4 awg for voltage drop, the panel gets to be full in a hurry.
You need to get wide tubs if you have more than a few of these CTs to install.
The ones I have worked with where made by Siemens.