This question concerns compliance with Article 430.102(A) for disconnecting means for a motor controller where the controller is integral to the MOV, yet the disconnecting means resides at the MCC and not within sight and when opened will disconnect power to the motor and controller.
By Article 430.102(B), an MCCB at a MCC qualifies as a disconnect for a motor on a MOV because it is capable of being locked in the open position, and the facility uses a lockout-tagout procedure and is maintained and operated by qualified personnel.
By Article 430.102(A), it would appear that another disconnect would be required at the MOV to satisfy the requirement for a controller disconnect.
1. Since the MCCB is a qualified disconnect for the motor, is it not equally qualified to serve as the disconnect for the controller at the MOV? (Control power for the controller is derived internally at the MOV from a control power transformer connected to the main line.)
2. In the above configuration, is an additional disconnect needed local to the MOV, if so why?