Sorry to be dense, but I am having a major mental block, so I would appreciate any input.
Where you have a starter that has a control circuit that is generated from the starter in Hand operation and in the Automated operation, the circuit is generated from the PLC, when the starter is in the "open" position, should all power sources be disconnected, specifically coming from the PLC? Or are you allowed under Exception No. 1(b) to put a permanent warning label stating that foreign voltage is present and stating the location of such.
Again, thanks for any insight and understanding.
Where you have a starter that has a control circuit that is generated from the starter in Hand operation and in the Automated operation, the circuit is generated from the PLC, when the starter is in the "open" position, should all power sources be disconnected, specifically coming from the PLC? Or are you allowed under Exception No. 1(b) to put a permanent warning label stating that foreign voltage is present and stating the location of such.
Again, thanks for any insight and understanding.