Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
Construction installed 2#12AWG's, plus #12 EGC from a typ lighting panelboard -20A 1P CB - to a small 1/2HP, 115V sump pump motor; a capacitor-run type with nameplate FLA of 7.5A. The motor has an internal thermal protector. The vendor flexible cord is around 10 feet long and is only #16AWG - (#12's from the panelboard tie into their plug). At first I thought it was ok, but looking 2017 NEC 430.6(A)(2)(1), it states FLC has to be used, not motor FLA which would be above the max allowable 8A, at 9.8A. Now I am thinking an additional fused disconnect needs to be placed near the motor to limit the cable ampacity per 240.4(D)(2).
Am I reading this right?
Am I reading this right?