I need a bit of help . HVAC crew at the shop installed a new heat pump system. condenser was "size for size" btu wise.
Existing unit was 4 ton wired with #10 THHN in EMT with (get this) a 20 Amp breaker. New unit wants a a minimum 42 Amp circuit, maximum breaker 45 Amp.
Now for my problem The #10's wont pull out of the pipe (best guess is a buried box). It is in a finished basement, so there is no easy way to repipe things without the obvious drywall removal.
Here is my question..... With a condenser load of 23 Amp (before any 125% factors), am I code compliant with the #10's on the 45? My interpretation is that I am, but I would like another opinion .
Thank you.
Howard