NEC Article 440.22 code interpretation question: An existing rooftop equipment is being replaced and is currently protected by 200A circuit breaker. new equipment has mca of 130, mocp of 175. Can the 200A circuit breaker be left and protect the #1/0 wiring with a fusible disconnect (200/175/3) at the rooftop unit? The 200A circuit breaker is still within 175% of the mca, but the unit has to be fused at 175. I guess my question is: with the addition of the fusible disconnect, are the wires from the panel now considered feeders and is normal wire sizing for 200A c/b (#3/0) applicable?