I didnt find this article 450.14 in 2008 code, any one have the 2011 and check. it is disconectmean for transformer requirement.
thanks
 

jumper

Senior Member
Here it is:

450.14 Disconnecting Means. Transformers, other than
Class 2 or Class 3 transformers, shall have a disconnecting
means located either in sight of the transformer or in
a remote location. Where located in a remote location,
the disconnecting means shall be lockable, and the location
shall be field marked on the transformer.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
For all practical purposes this new 2011 rule only requires the addition of a label on the transformer. It would be a rare case where the primary OCPD was not also a disconnect. That is assuming that the primary OCPD is remote from the transformer. If the OCPD is within sight, then there is no change.
 