So I notice that article 502.6 allows for equipment suitable to 506.9 to be installed in Class II locations.
Is there an allowance within 506 for the vice versa? We are looking at supplying equipment to satisfy the requirements of 506 but there may be one or two items that can only be sourced as per the those equipment requirements and so may meet the 502 requirements.
506.7 does not allow the Class and Division classification to overlap the Zone classification so as I read it for the Zone classification method (Art 506) only equipment marked as per that article is acceptable? Am I missing something?