Bill Annett
Senior Member
- Location
- Wheeling, WV
- Occupation
- Retired ( 2020 ) City Electrical inspector
I am the Electrical Inspector for a small city. I have held this position for over 7 years. I read this forum every day. I have learned alot from its members. I learn more and more every day.
In my 7 years i have only inspected 1 gas station. I am currently inspecting another. I have told the electrical contractor that i felt that something was not meeting the 2005 NEC.
Here is the situation. From the pumps(seal offs are installed) Rigid metal conduit ( RMC) is installed on about the first 10 feet of the run towards the Building(convienience store). It goes down 24 inches below grade and connects to rigid nonmetallic conduit (RNC). This RNC now enters the store below slab. This end does not have the 10 feet of RMC. This end has less than 1 foot of RMC below grade. Seal offs are installed at the top of the floor
I told him that you need at least 2 feet of RMC below the floor. I am basing my opinion from article 514.8 of the 2005 NEC.
On Monday I am having a meeting with the contractor and the owner or the gas station.
Any information which you can give me will be appriciated. If I am right or wrong, I have to know. I want to get this right. Like i said I am learning every day and this is part of that learning experiance.
I want to thank every one who replies. I nay not be able to get back on line until Monday.
Thanks Again, Bill
In my 7 years i have only inspected 1 gas station. I am currently inspecting another. I have told the electrical contractor that i felt that something was not meeting the 2005 NEC.
Here is the situation. From the pumps(seal offs are installed) Rigid metal conduit ( RMC) is installed on about the first 10 feet of the run towards the Building(convienience store). It goes down 24 inches below grade and connects to rigid nonmetallic conduit (RNC). This RNC now enters the store below slab. This end does not have the 10 feet of RMC. This end has less than 1 foot of RMC below grade. Seal offs are installed at the top of the floor
I told him that you need at least 2 feet of RMC below the floor. I am basing my opinion from article 514.8 of the 2005 NEC.
On Monday I am having a meeting with the contractor and the owner or the gas station.
Any information which you can give me will be appriciated. If I am right or wrong, I have to know. I want to get this right. Like i said I am learning every day and this is part of that learning experiance.
I want to thank every one who replies. I nay not be able to get back on line until Monday.
Thanks Again, Bill