I have a hypothetical bulk storage plant where there are tanks outside, and processing vessels, piping, and pumps both inside and outside. None of the vessels, pipes, or pumps will release vapor or fluid in normal operation. Chemicals are piped in, not poured. The only flammable chemical present is methanol (Class 1 Group D).
The current plan is to locate the control room and a lab to test various samples inside the building with the processing vessels. And the plan is to have doors opening inside to the main plant floor, albeit a good distance from the processing equipment.
My confusion is, the code defines limited zones around tanks that div 1 and div 2, if the tanks are sometimes opened for filling purposes. After some distance, we're unclassified again. It defines these distances whether such a tank is inside or outside.
Then it says in table 515.3 under "tank storage installations inside buildings" (if I'm interpreting correctly) that the presence of a tank that is never vented to the air automatically makes everything inside the building Class 1 Div 2.
If I read table 515.3 correctly, if I can open it up to pour more in, I'm only Class 1 Div 2 for so far away, but if I never open it, if it fills & drains through pipes, I'm class 1 Div 2 wall to wall to floor to ceiling, and class 1 divi 1 if I have a trench below grade.
Why would a tank or vessel that I open and release fluid and vapor from be safer than a tank that I never normally open and never release fluid or vapor from?
Table 515.3 also declares offices and rest rooms unclassified if they don't open to the classified area, or if they do, if the classified area doesn't reach the door. If the classified area reaches the door, by code, you behave as though the wall doesn't exist. This is where the hair splitting on whether the whole inside is class 1 div 2, or just regions so far away from pumps and vessels are class 1 div 2.
If I go by the criteria of opening vessels, the doors can be moved far enough away from the nearest vessel full of flammables. If I go by "tank storage installations inside buildings" the whole inside above floor grade is class 1 div 2. If I go by "indoor equipment installed in accordance with 5.3 of NFPA 30" I have defined distances. Same for my pumps.
What will it be?
Also, the rule on indoor office space and rest rooms specifies distance from openings indoors, not outdoors. Does this mean I can have the door next to a big methanol vessel outside and its zone won't extend into my room due to the door as it would were the door and vessel inside?
At some point the hazardous area must end, and it would be nice if the NEC gave one clear answer.
I can always move the doors outside, but I'd rather not.
How should I interpret this article of the NEC as well as NFPA 30?
The current plan is to locate the control room and a lab to test various samples inside the building with the processing vessels. And the plan is to have doors opening inside to the main plant floor, albeit a good distance from the processing equipment.
My confusion is, the code defines limited zones around tanks that div 1 and div 2, if the tanks are sometimes opened for filling purposes. After some distance, we're unclassified again. It defines these distances whether such a tank is inside or outside.
Then it says in table 515.3 under "tank storage installations inside buildings" (if I'm interpreting correctly) that the presence of a tank that is never vented to the air automatically makes everything inside the building Class 1 Div 2.
If I read table 515.3 correctly, if I can open it up to pour more in, I'm only Class 1 Div 2 for so far away, but if I never open it, if it fills & drains through pipes, I'm class 1 Div 2 wall to wall to floor to ceiling, and class 1 divi 1 if I have a trench below grade.
Why would a tank or vessel that I open and release fluid and vapor from be safer than a tank that I never normally open and never release fluid or vapor from?
Table 515.3 also declares offices and rest rooms unclassified if they don't open to the classified area, or if they do, if the classified area doesn't reach the door. If the classified area reaches the door, by code, you behave as though the wall doesn't exist. This is where the hair splitting on whether the whole inside is class 1 div 2, or just regions so far away from pumps and vessels are class 1 div 2.
If I go by the criteria of opening vessels, the doors can be moved far enough away from the nearest vessel full of flammables. If I go by "tank storage installations inside buildings" the whole inside above floor grade is class 1 div 2. If I go by "indoor equipment installed in accordance with 5.3 of NFPA 30" I have defined distances. Same for my pumps.
What will it be?
Also, the rule on indoor office space and rest rooms specifies distance from openings indoors, not outdoors. Does this mean I can have the door next to a big methanol vessel outside and its zone won't extend into my room due to the door as it would were the door and vessel inside?
At some point the hazardous area must end, and it would be nice if the NEC gave one clear answer.
I can always move the doors outside, but I'd rather not.
How should I interpret this article of the NEC as well as NFPA 30?