Some research has convinced me that Article 517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas is intended to require redundant grounding systems in patient care areas--one consisting of a metallic raceway system, and the other consisting of insulated copper conductors. However, nowhere in this section does the word "redundant" appear. Nor does paragraph B stipulate the extent of the insulated copper conductors.
Question: If the authors of the Code want redundant grounding, why doesn't the article read something like,
Patient care areas shall be provided with redundant grounding systems consisting of a metal raceway system installed in accordance with 250.118 and a system of insulated copper grounding conductors extending from all receptacles and fixed equipment to a common grounding point in the grounding electrode system.
As written, the article could be interpreted to mean that the insulated copper conductors could be terminated at the outlet box that is part of the raceway system. In fact, the Handbook asserts that it is not necessary to run a separate, insulated equipment grounding conductor to the branch circuit panelboard wehre the feeder wiring method is recognized as an equipment grounding conductor per 250.118.
Question: If the authors of the Code want redundant grounding, why doesn't the article read something like,
Patient care areas shall be provided with redundant grounding systems consisting of a metal raceway system installed in accordance with 250.118 and a system of insulated copper grounding conductors extending from all receptacles and fixed equipment to a common grounding point in the grounding electrode system.
As written, the article could be interpreted to mean that the insulated copper conductors could be terminated at the outlet box that is part of the raceway system. In fact, the Handbook asserts that it is not necessary to run a separate, insulated equipment grounding conductor to the branch circuit panelboard wehre the feeder wiring method is recognized as an equipment grounding conductor per 250.118.