The 2005 was very different -
Where did 2005 come up in the post?
The ROP that clarified this issue for the 2008 revision made it clear that the ATS feeders for the different emergency, legally required or optional loads could originate in switchgear, but not panelboards.
Panel Meeting Action: Accept in Principle
Revise existing section 700.9(B) by adding a new Number (5) to (B) to read as
follows:
(5) Wiring from an emergency source shall be permitted to supply any
combination of emergency, legally required, or optional loads in accordance
with (a), (b) and (c).
(a)From separate sections of a vertical switchboard, with or without a
common bus, or from individual disconnects mounted in separate enclosures.
(b)The common bus or separate sections of the switchboard or the individual
enclosures shall be permitted to be supplied by single or multiple feeders
without overcurrent protection at the source.
(c)Legally required and optional standby circuits shall not originate from the
same vertical switchboard section, panelboard enclosure or individual
disconnect enclosure as emergency circuits.
Exception to (5) (b). Overcurrent protection shall be permitted at the source or
for the equipment, provided the overcurrent protection is selectively
coordinated with the down stream overcurrent protection.
Emphasis added
Panel Statement: The panel has placed revised text in a new list Item (5) in
Section 700.9 (B) to clearly identify that the original separation requirements
from the source to the loads or from the source distribution overcurrent
protection to the loads is to remain unless modified by (1) ? (5).
The revised text will further clarify that it is permitted to supply any
combination of emergency, legally required or optional loads from a single
feeder or from multiple feeders or
from separate vertical sections of a
switchboard that are supplied by either a common bus or individually.
The use of an overcurrent protective device at the source or for the equipment
is a matter of reliability and design. While the requirements in (5) (b) maintain
the highest degree of reliability, the exception to (5) (b) will permit the use of
an overcurrent device at the source or for the equipment. The coordination of
the overcurrent protection at the source or for the equipment with the
downstream overcurrent protection requirement in the exception will maintain
the highest degree of reliability possible while allowing protection for
conductors and equipment. The revised text in the main paragraph should also
make it clear that circuits supplying emergency loads
are not to be combined in
panelboard enclosures with circuits supplying other loads.