Article 555 - GFCI Protection

Status
Not open for further replies.

Npstewart

Senior Member
Im working on a new floating structure under the NEC 2011. We have a small condensate pump (208v - Single Phase) that is currently fed from a GFCI breaker located within the panel, within the floating structure. The GFCI breaker keeps tripping after the pump cycles on. Does anyone know if Article 555 requires all branch circuits within a panel to be GFCI protected, even if they are NOT 120v?
 
Im working on a new floating structure under the NEC 2011. We have a small condensate pump (208v - Single Phase) that is currently fed from a GFCI breaker located within the panel, within the floating structure. The GFCI breaker keeps tripping after the pump cycles on. Does anyone know if Article 555 requires all branch circuits within a panel to be GFCI protected, even if they are NOT 120v?
Whether GFCI is required or not, I think you need to figure out what is wrong.

Might be tripping on overload instead of GFCI, in which case you will still have the problem if you eliminate GFCI.
 
Im working on a new floating structure under the NEC 2011. We have a small condensate pump (208v - Single Phase) that is currently fed from a GFCI breaker located within the panel, within the floating structure. The GFCI breaker keeps tripping after the pump cycles on. Does anyone know if Article 555 requires all branch circuits within a panel to be GFCI protected, even if they are NOT 120v?

I do not believe it does but I would be asking first, why is it tripping rather than can I remove it. Code be damned, life safety first.
 