Is SJ cable flexible cable allowed under a raised floor utilizing Article 645? I say no. Here's where I think I am obligated to...
"Article 645 Information Technology Equipment
645.5 Supply Circuits and Interconnecting Cables
(D) Under Raised Floors
(5) Cables, other than those covered in (D)(2) and those complying with (D)(5)(a), (D)(5)(b), or (D)(5)(c), shall be listed as Type DP cable having adequate fire-resistant characteristics suitable for use under raised floors of an information technology equipment room."
The SJ flexible cord runs from the receptacles under the raised floor to the IT equipment. I looked for type DP cable on the internet and didn't have any luck. Is this type cable common? Thanks.