Delete entire second paragraph of 680.32. Add new text as second line of first
paragraph:
The ground-fault-circuit interrupter shall be an integral part of the attachment
plug or located in the power supply cord within 300 mm (12 in.) of the
attachment plug.
Substantiation: The above proposal was adopted by CMP-17 during the last
Code cycle, but was placed on hold by the TCC. The reason for the TCC hold
was that the Panel proposal (Log #CC1700) to address TIA 02.2 introduced
new material not presented during the ROP phase.
The intent of this proposal is to submit the panel?s proposal during the ROP
in order to have the panel?s position properly incorporated in the next edition of
NFPA 70.
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Accept in Principle in Part
Change 680.31 to read as follows:
680.31 Pumps
A cord-connected pool filter pump shall incorporate an approved system of
double insulation or its equivalent and shall be provided with means for
grounding only the internal and nonaccessible non?current-carrying metal parts
of the appliance.
The means for grounding shall be an equipment grounding conductor run with
the power-supply conductors in the flexible cord that is properly terminated in
a grounding-type attachment plug having a fixed grounding contact member.
Cord-connected pool filter pumps shall be provided with a ground-fault
circuit interrupter that is an integral part of the attachment plug or located in
the power supply cord within 300 mm (12 in.) of the attachment plug.
Panel Statement: The panel accepts the submitter?s recommendation to add
two new paragraphs. However, these were combined and relocated to 680.31
for clarity.
The panel chose to retain ?All 125-volt receptacles ? barrier? in 680.32.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 10 Negative: 1
Explanation of Negative:
HIRSCH, B.: The EEI/EL&P believe the current code wording amply covers
the GFCI requirements. The change does not offer any additional protection for
the public and in the case of pool pumps will require duplicate GFCI
protection. In addition, requirements for pool pump cords should be covered in
the appliance standards and not in the NEC. The submitter did not provide
substantiation for the change, but simply that the proposal was placed on hold
by the TCC during the 2005 comment cycle due to being new material.