For an above ground pool:
1) How far can the heater and filter be placed from the pool?
Article 680.12 states "...Each means shall be readily accessible and within sight from its equipment and shall be located at least 5 ft horizontally from the inside walls of a pool..." If I am reading this correctly, if the disconnect for the heater, and the heater, are located 25' from the inside wall of the pool, this would be acceptable, correct?
Article 680.22(A)(1) states "...Receptacles that provide power for water-pump motors or for other loads directly related to the circulation and sanitation system shall be located at least 10 ft from the inside walls of the pool..." If I am reading this correctly, if the filter receptacle, and the filter, are located 25' from the inside wall of the pool, this would be acceptable, correct?
2) The heater specs call for a 60A maximum fuse size, and Minimum Circuit Ampacity of 35A. So this would require a 60A breaker, and 6 AWG wire, correct?
3) Does the pool heater require GFCI protection?
Thanks in advance.
Thanks in advance.