Please clarify when PVC, above ground junction boxes are required to have ground lugs.
Welcome to the forum. I don't know when nor do I know what art. 680 has to do with it. I do believe that the ground lug is required because of the metal threads for the screws.
 
Article 680

If I use all pvc connections to the wet niche light ( No brass or steel counduit) wire nut all grounds together, Is it required to use a pvc box with a ground bar and lugs. I can see using only if brass or steel is used as a raceway.
 
If pvc conduit is used, and all grounds spliced in above ground box, No brass or steel conduit is being used, why would I need a pvc J-Box with a ground bar? I can see this only if brass or steel is used from the wet niche light to the PVC J-Box. Intermatic PJB2175 or PJB4175. I would use this box when using metal raceway. If not a standard PVC J-box ( with no lugs ) should be correct when using all pvc raceway.
 
Check 680.24 for the requirements for a junction box for Pool Underwater Luminaries. You will note specific specification and also the requirement that the box be listed.
Few, if any, jurisdictions accept a "off the shelf" box for this purpose.
 
Check 680.24 for the requirements for a junction box for Pool Underwater Luminaries. You will note specific specification and also the requirement that the box be listed.
Few, if any, jurisdictions accept a "off the shelf" box for this purpose.
I didn't know they made a PVC pool junction box.
 
You've got a large mix in wire sizes to interconnect. Will most likely have a #8 copper from the forming shell, the EGC in the light cable (probably #14 or #16), and a #12 or larger EGC from the branch circuit source. Is there a wire nut that will take that wire combination? How about a split bolt? A multi lug terminal is designed just for that type of application.

Finally, code says you have to terminate these bonding conductors on terminals.
 